One thing I wanted to mention was that I think your price point is a little high and that might deter people from considering spray foam. As a project manager for a spray foam company for years I can tell you that we offer 0.5 Lb. open-cell foam at around $.25/board foot. We even offer a 1.0 Lb. open-cell foam for less/the same cost as you quoted the 0.5 Lb. foam for above. The 1/0 Lb. open-cell foam has an R-value of almost 5.


In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides).
The video below is from a house near Charleston, South Carolina that I visited recently, and you'll see that the homeowner in this case didn't get his money's worth. I knew immediately when I walked into the attic that something was wrong because it was hot up there. In a properly insulated spray foam attic, the temperature won't be much higher than the house temperature. 
Q. "I talked to a building product supplier for WALLTITE spray foam, he is suggesting to use 2" or 3" of closed cell-spray foam in the joists areas instead of the batts insulation. He says it will work with outboard rigid insulation. There is a location of a cantilevered floor area with steel beam so I may need to use spray foam to protect the steel beam. It would then be convenient continue to spray in the floor joist cavities and then apply 5" of polyiso outboard of the bottom cantilever floor sheathing."

How Much Is A Board Foot Of Spray Foam


That’s $58.3 Billion dollars. That’s roughly how much money we wasted in 2010 in the US according to the Department of Energy because of air leaking out of our building envelopes. If your building leaks energy, you’re paying more for energy than you need to. Clearly you’re not alone. If you’re ready to claim your share of the savings, it’s quicker and easier than you think.

Spray Foam Insulation


Clean and free the roof surface of any debris and then dry the surface using a cloth. If you happen to have a current coating on the surface, check for adhesion. Consider removing loose coating, repairing, cleaning and then checking the area. Remember to use Energy Guard without thinning it because it is sold ready for use. Containers should not be left open except for a short period of time. You must also ensure that you check for any existing coating adhesion before opening Energy Guard. For application, you will require a brush preferably a bristle brush (synthetic) or a short nap roller. You can also use a good airless sprayer with a 0.031 or 0.027 tip to apply the coatings at (3000 psi/1gpm). You will also need water for cleaning up when you are done. https://youtube.com/watch?feature=youtu.be&v=ggLAUsiuI_o
This high R-value of 4.45 at 1 inch, polyurethane insulation expands to seal cracks, gaps, and voids in attics, walls, crawl spaces, and ceilings. Agribalance is a three-quarter pound density foam that reduces air leakage by improving energy efficiency, and reducing moisture intrusion and outside contaminants such as dust, dirt, and allergens. As a result, builders can generally install smaller, more energy-efficient HVAC systems and achieve similar, or superior comfort compared to traditionally insulated structures which require a larger, less efficient HVAC system – resulting in higher energy costs.
Spray foam insulation is typically priced by volume, meaning your cost will depend on how much material you need to use to insulate your space, although other factors may influence price as well. In most cases, the cost of spray foam insulation is more than worth it, as it's a once and done upgrade that will not only provide energy savings in your home, but also improve your home's overall comfort.

One of the high-tech insulation products being utilized these days is a foam-spray product called "Icynene," which is a foam that starts as two liquid components (a and b, if you will) that are heated up and sent through two hoses and meet at a tip of a gun where the magic begins. This is a thin film that expands to 100 times its volume in eight seconds, when it's permanently set up. https://www.youtube.com/embed/ggLAUsiuI_o
I don't even want to ask this question but... several years ago we hired a local contractor to spray high density foam on the roof deck and walls of our unfinished 2nd floor. We realized that the job was done poorly and cut an access into the attic space to assess things. We realize now that they spray foamed directly to the chimney (no flashing). The chimney is currently used for a woodstove and DHW venting. The DHW will go away but wood stove will remain. My question is, how bad (unsafe) is this? I have found information on foam exposure to fire but have not been able to find anything about temperature ratings in general (i.e. what happens on prolonged exposure to high temperatures).
As this example illustrates, it's important to seal the envelope completely. One of spray foam's biggest selling points is its air-sealing ability, but it can't seal places where it's not sprayed. One of the nice things about using spray foam in new construction is that you can do a Blower Door test before the drywall goes in. Even better, you can test for leaks with a fog machine.
Henry 587 Dura-Brite White Elastomeric Roof Coating is Henry 587 Dura-Brite White Elastomeric Roof Coating is a premium high solids formula offering better weather protection solar reflectivity and longevity than economy grade reflective roof coatings. Cured coating forms a permeable membrane which prevents liquid infiltration but allows moisture vapor to vent or breathe out of underlying substrate. Recommended ...  More + Product Details Close
Heat which is created elsewhere that is transported by means of a fluid, such as water or in our case air. Spray foam insulation's most important attribute is the ability to air seal creating a custom airtight envelope within the building structure. The added benefit to air sealing is the ability to block convective heat transfer from interior to exterior during heating months and vice versa during cooling months, as the heat cannot escape through gaps in the buildings envelope without the aid of air movement from infiltration as a means of transport.
In the early days of insulating attics, people believed the insulation was a heat source. That’s not the case, as the insulation is actually a barrier between two areas of different temperatures. As for the “hot roof” theory, the unvented attic system could make the temperature of the roof go up a little, but this increase won’t cause damage to your shingles. https://youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o
I live in Baton Rouge LA with a very old and drafty house. There is no blockages in the walls between the crawl space and attic. Lots of critters just come on in. I would like to used closed cell sprayed under house to warm up floors and block moisture. I would like to spray closed cell into attic, but am afraid of enclosing attic due to moisture build-up. Can I spray closed cell against the attic floor in same way as installing bats, thus leaving my venting the same as it always has been. Other ideas? Thanks.
Clean and free the roof surface of any debris and then dry the surface using a cloth. If you happen to have a current coating on the surface, check for adhesion. Consider removing loose coating, repairing, cleaning and then checking the area. Remember to use Energy Guard without thinning it because it is sold ready for use. Containers should not be left open except for a short period of time. You must also ensure that you check for any existing coating adhesion before opening Energy Guard. For application, you will require a brush preferably a bristle brush (synthetic) or a short nap roller. You can also use a good airless sprayer with a 0.031 or 0.027 tip to apply the coatings at (3000 psi/1gpm). You will also need water for cleaning up when you are done.
I don't know if it's common or uncommon, but installing a layer of rigid foam above your roof sheathing in order to interrupt thermal bridging is always a good idea, and is preferable in all respects to a roof assembly without any rigid foam above the sheathing. If you decide to install rigid foam above the roof sheathing, you shouldn't use closed-cell spray foam under the sheathing; either use open-cell spray foam (which is vapor-permeable) or a fluffy insulation like cellulose, mineral wool, or fiberglass (any of which will allow the roof sheathing to dry to the interior). https://youtube.com/watch?v=ggLAUsiuI_o&app=desktop
The Canadian National Building Code references the CAN/ULC S705.2 National Application Standard which must be followed during all installations of 2lb medium density closed cell polyurethane foam. Every installer of CAN/ULC-S705.1 compliant medium density, spray applied foam must be licensed in order to spray foam and hold valid photo ID issued by their Quality Assurance Program (QAP) provider showing their license is in good standing.
Warning: EnergyGuard™ Elastomeric Roof Coatings can freeze below 32° F. This is because the product is water based. In case of freezing temperatures, stop the application process. After application, you must allow the product time to dry before exposing the elastomeric roof coating to foot traffic or water. You should also cover the containers and dispose them responsibly after application. In case you or someone else i.e. a child ingests the coating seek immediate medical attention. Don't induce vomiting.
What do you mean by "our AC units require fresh air ventilation"? Fresh air doesn't come from the attic. If there's an atmospheric combustion appliance in the attic, such as an 80 AFUE furnace, then you shouldn't be encapsulating the attic anyway. If that's the case, you don't want spray foam on the roofline at all. You can either change out the furnace to a sealed combustion unit or do your insulating and air-sealing at the flat-ceiling level.
One of the high-tech insulation products being utilized these days is a foam-spray product called "Icynene," which is a foam that starts as two liquid components (a and b, if you will) that are heated up and sent through two hoses and meet at a tip of a gun where the magic begins. This is a thin film that expands to 100 times its volume in eight seconds, when it's permanently set up.

I recently did a remodel project for my basement using spray foam insulation. The original builder has used fiberglass, but I wanted the best insulation i could find. We chose closed cell foam because it blocks moisture from getting into the house. It took one day to install and was fumey for about 3 hours. It was pretty cool watching it being done. It comes out as a liquid and then expands rapidly into a foam. It's quick! Then they took a types of saw to shave it flat with the wall studs so we could then go ahead and drywall.
Spray foam is a fully adhered insulation that is spray applied into wall cavities, providing a continuous air and moisture barrier. Spray foam allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. Spray foam effectively seals the building envelope, filling in any cracks and crevices, the common source of air and moisture infiltration as well as temperature variations.
If you’re not familiar, spray foam is a type of insulation that expands after you spray. The foam expands and seals, avoiding any type of unnecessary moisture (which can create mold) or encouraging pests to eat through your walls. It protects the lining of your house, and even can protect the heating and cooling of your house during those unbearably cold or hot days.

A: The RV roof coating works by waterproofing, weatherproofing and sealing our RV roofs from elements, including rain, snow, wind and other outer forces. It can also resist impact from leaves, twigs, dusts and other things that would otherwise damage the roof. It also works by reflecting UV rays, keeping the roof from degradation. The roof coating can also prevent leaks, heating and cooling loss and discomfort in our RV. https://www.youtube.com/watch?feature=youtu.be&v=ggLAUsiuI_o
Part of that guidance will be explaining that interior, two component foam is applied with the professional using specific personal protective equipment (high-pressure foam is installed while using a respirator, for example). It is encouraged that professionals explain clearly to customers that this equipment, coupled with certain work and engineering practices, including ventilation, is used to minimize exposures to the chemicals used to make SPF during the job.
These coatings are emulsified asphalt and consist of asphalt particles dispersed in water; they utilize clay as the emulsifying component. These coatings also contain many types of organic and/or inorganic fibers and fillers to provide extra strength to the coating. These coatings are available in black, brown, or as a reflective coating when titanium dioxide or aluminum pigments are added.

Check with the coating manufacturer who may be able to suggest applicators who have used their products and have familiarity with the application. Another option would be to interview contractors and ask specific questions about their proven ability to install roof coatings. Contractors affiliated with the National Roofing Contractors Association (NRCA) or local roofing contractor trade associations typically are more knowledgeable. Consult those groups’ websites for contractors.
We have a 1950's ranch in Atlanta and are interviewing foam contractors to spray open cell under the roof, with an "ankle wall" out towards the eaves to seal the attic. My wife and daughters are chemically sensitive, so I'm trying to figure out how to minimize the fumes coming into the house. Additionally, at least one contractor has offered (for > $900) to remove our existing rock wool & R-13 fibreglass from the attic floor to "increase cross-ventilation into the attic". Seems to me I can't both minimize fumes AND increase cross-ventilation. They also offered to spray a fire-retardant on for >$600. Would ventilation during installation help any or woud the retardant seal off the foam and help that way? Thanks...
You probably have some familiarity with spray foam insulation, and you may have even used the foam that comes in pressured spray cans at home improvement retailers. This foam is know as one-part foam, meaning that it is one continuous mixture that is simply applied to the area in need. One-part foam is frequently used for sealing small gaps and cracks.
In the case you have above the installer wasn't reading his foam. They must be trained to do that as they spray. Temps and conditions are constantly changing thru out the day. Either he wasn't properly trained or if he was,he wasn't doing his job! This is a serious problem with people jumping in to the foam business. A lot of homeowners and builders are looking the best price and end up with someone who doesn't know what they are doing. Hope this info helps. Foam insulation is a great product. It just has to be done right by someone who knows what they are doing.

Spray Foam Sealant


Ames® elastomeric waterproof roof coatings are premium coatings that seal out moisture, renew old surfaces and even save energy. We have products specifically formulated for all types of roofs including; Wood, Tar, Metal, Rolled Roofing, EPDM Rubber, Foam and many other surfaces. From flat roof coating to plywood roof coating, Ames’ liquid rubber roof paint coatings form a waterproof seal to preserve and protect your roof. Our white roof coatings reflect sunlight, substantially reducing roof temperatures and helping you save on cooling costs. Ames® products are environmentally friendly, water-based, non-toxic, VOC-free and can be cleaned with water. If you’re looking for how to seal a flat roof, pitched rolled roof, or just about any other kind, our elastomeric waterproof roof coatings can help you get the job done.
Q. "I talked to a building product supplier for WALLTITE spray foam, he is suggesting to use 2" or 3" of closed cell-spray foam in the joists areas instead of the batts insulation. He says it will work with outboard rigid insulation. There is a location of a cantilevered floor area with steel beam so I may need to use spray foam to protect the steel beam. It would then be convenient continue to spray in the floor joist cavities and then apply 5" of polyiso outboard of the bottom cantilever floor sheathing."
Spray foam insulation works by sealing the building envelope to stop conditioned air from escaping and prevent unwanted outside air from entering your home. It allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. It's a lightweight, durable, and versatile insulation solution boasting the industry’s strongest performance in energy efficiency and energy cost savings.

How Much Is Spray Foam Insulation Installed

×