Open-cell is also known as half-pound foam. It has an R-Value of 3.5-3.6 per inch, and its density is bout 0.5 pounds per cubic food. Low-density foams like these are made partially from raw biological materials Carbon dioxide or water is also used in the makeup. Open-cell uses far less material than closed-cell, but its R-Value is lower. Also, open cell requires a vapor retarder (like gypsum wallboard) and is riskier when used for roof sheathing. It's not highly recommended that you use open-cell insulation if you live in a cold climate unless you have that extra barrier. You should also compare how much money you spend versus how effective the open-cell insulation is wherever it's installed. http://y2u.be/ggLAUsiuI_o
Although spray polyurethane foam has many advantages over other types of insulation, spray foam installation isn’t foolproof. Some builders have reported problems with sloppy foam insulation. For example, some installers have been known to begin spraying before the chemical components are up to temperature, which can affect component mixing and foam performance. When components are poorly mixed, or mixed in the wrong ratio or at the wrong temperature, cured foam has been known to shrink away from rafters or studs, leaving cracks. Some installers rush through their spraying, resulting in voids. https://www.youtube.com/watch?v=ggLAUsiuI_o&feature=youtu.be
once the foam is installed correctly, it is a inert plastic not much different than the foam cushions you sit on. there is not a health rick unless you have off ratio uncured foam that has not mixed properly. the foam is absolutely a health risk in its raw forms before it is mixed and cured. You should not be in the building without proper respirators and eye protection. The spray foam industry should be controlled and regulated by the same standards, testing and inspections that framing ,electrical and plumbing are. until that happens then you will have idiots with spray rigs ruining peoples homes and ruining the market for honest foam contractors that know how to price a job fairly and complete it correctly.

How Much Is Open Cell Spray Foam Insulation


Most flat roofs are not perfectly sloped, causing water to puddle in some areas, in particular around the drains and scuppers. Many roof coatings are not rated or warranted for "ponding water", and thus might fail pre-maturely if exposed to standing water over long periods of time. Serious consideration should be given to the performance and limitations of the coating being selected. Some manufacturers will warranty their coatings including ponding water. Typically, manufacturers for acrylic roof coatings do not include warranties for ponding water, while some polyurethane and silicone roof coatings manufacturers will.
Spray foam insulation, like other insulation, saves on energy costs and lowers utility bills. Studies by the US Department of Energy show that 40% of a home's energy is lost as the result of air infiltration through walls, windows and doorways. Buildings treated with spray foam insulation insulate as much as 50% better than traditional insulation products.
Fort Worth, Arlington, Denton, Lewisville, North Richland Hills, Haltom City, Weatherford, Flower Mound, Keller, Grapevine, Bedford, Euless, Granbury, Hurst, Stephenville, Carrollton, Mineral Wells, Frisco, Azle, Crowley, Southlake, Rhome, Haslet, Aubrey, Colleyville, Dublin, Grand Prairie, The Colony, Dallas, Lake Dallas, Sanger, Kennedale, Little Elm, Roanoke, Decatur, Pilot Point, Mansfield, Poolville, Aledo, Argyle
For maximum durability and leak resistance, we recommend that two coats of topcoat be applied at 100 sq. ft. per gallon, or a minimum of 20 mils dry coating. If two complete topcoats are not applied, always apply two thick coats to problem areas such as scuppers, drain areas, ponding areas, seams, and repaired areas. Avoid using Elastek Solar Magic™ or The Shield™ on ponding roofs. Clean skin and tools promptly with water.
Please Note: Prices, promotions, styles and availability may vary by store and online. Inventory is sold and received continuously throughout the day; therefore, the quantity shown may not be available when you get to the store. This inventory may include a store display unit. Online orders and products purchased in-store qualify for rebate redemption. Mail-in Rebate is in the form of merchandise credit check, valid in-store only. Merchandise credit check is not valid towards purchases made on MENARDS.COM®. By submitting this rebate form, you agree to resolve any disputes related to rebate redemption by binding arbitration and you waive any right to file or participate in a class action. Terms and conditions available at www.rebateinternational.com®

Repair and seal roof penetrations, tears, open seams, etc. using Elastek 103 Crack & Joint Sealant and reinforce with polyester roof fabric as necessary. In larger or deep ponding areas, apply Elastek 500 Puddle Plaster to fill in areas that hold water. Avoid using plastic roof cement. Serious ponding should be referred to a roofing contractor. Blisters in previous coatings may be opened but these areas must be allowed to dry-out completely. Blisters in the roofing ply should be left alone unless likely to break. Caulk and reinforce open seams, roof penetrations, cracks, and tears. These are potential leak points so work carefully and thoroughly. Use fabric to build flashings around roof edges or roof penetrations, and to reinforce various coating repairs. A polyester fabric is used because it will stretch with the coatings. (Fiberglas fabric is not recommended.) Fabric is normally cut to extend three inches beyond the repaired area in all directions. The coating is applied to the roof surface and the fabric is immediately pushed into the wet surface. An additional coat is applied over the fabric and the patch is allowed to dry. If your roof has stucco parapets, examine them for cracks along the sides and top. These areas often permit water to enter the wall and can cause blisters and wrinkles in the roof surface. Repair with Elastek 103 Crack & Joint Sealant. If you do not have parapets, examine the metal drip edge for a tight seal with the roof membrane. Use 4″ or 6″ roofing fabric covered under and over with Crack & Joint Sealant to seal cracks along drip edges, penetrations, and open seams. https://m.youtube.com/embed/ggLAUsiuI_o


I have to insulate my walls at the end of this week. That does not give me time to procure slow-rise foam, so my stud cavities will be filled with foam before I'm ready to fill the corner voids. I will not be able to drill straight through the corner studs. Instead, I will have to remove material where the studs meet. What sort of tool do you envisioning me holding while I create space to pump foam into my 1972 corner voids?

Spray Foam


I am building a house in Central Texas (Caldwell). Several builders are cautious about using foam insulation and/or a closed attic. I would like to use both. Here in Texas, heat and humidity (except for the past few years of drought) are a continuing problem. Which type of foam would be the best to use in our home, where should the vapor barrier be or should be use one at all, if we are using fans in the exterior walls to supply fresh air to the house, do we need a vented attic or will it cause more problems than it solve? I have printed out your article and the blogs to give to my contractors and architect, but I would really appreciate your comments on the products being used in my part of the US. 


One thing I wanted to mention was that I think your price point is a little high and that might deter people from considering spray foam. As a project manager for a spray foam company for years I can tell you that we offer 0.5 Lb. open-cell foam at around $.25/board foot. We even offer a 1.0 Lb. open-cell foam for less/the same cost as you quoted the 0.5 Lb. foam for above. The 1/0 Lb. open-cell foam has an R-value of almost 5.
What more is that we also think it is one of the most durable among liquid roof coatings on the market. It can last for several years, working continuously in protecting your roof from outside elements, such as dust, leaves, twigs and debris that would otherwise damage your roof. When it happens, your roof might have leaks and cause discomfort inside your RV. https://www.youtube.com/v/ggLAUsiuI_o
In the early days of insulating attics, people believed the insulation was a heat source. That’s not the case, as the insulation is actually a barrier between two areas of different temperatures. As for the “hot roof” theory, the unvented attic system could make the temperature of the roof go up a little, but this increase won’t cause damage to your shingles.
The RV roof coating is a sealing, weatherproofing and waterproofing product that is used in recreational vehicles, campers and trailers, to name some. It works effectively in sealing the roof’s membrane from water and moisture that would otherwise build up and cause damage to the roof. When unattended, the buildup can eventually leads to leaks inside the RV, causing so much discomfort to your loved ones.

Having a recreational vehicle, see to it that you protect its roof from anything that would otherwise damage it or decrease its lifespan. One of the best maintenance and repair products you need is the best RV roof coating. It can offer you a host of benefits we’ve mentioned above, so it is really necessary for your RV cleaning and maintenance products arsenal. Pick based on those we’ve featured here as well as on certain factors, including your roof material, for the desired results. Did you like this guide? Share it on Facebook today! If you’re looking for more products in RV cleaning and maintenance, then I suggest going for these articles: best RV wash and wax, best RV roof sealants, best RV caulks, best RV wax, best RV roof cleaners and best RV awning cleaners. I do hope you will like them. Happy shopping!
Spray foam insulation, like other insulation, saves on energy costs and lowers utility bills. Studies by the US Department of Energy show that 40% of a home's energy is lost as the result of air infiltration through walls, windows and doorways. Buildings treated with spray foam insulation insulate as much as 50% better than traditional insulation products.

Today’s “third generation” of blowing agents have a GWP of 700 to 1000 which is still remarkably high considering water/CO2 has a GWP of 1. However, innovation from some chemical manufacturers like the Chemours Company have introduced the next generation of HFO blowing agents such as Opteon 1100, which significantly reduces the GWP impact when using closed-cell spray foam insulation products.
You probably have some familiarity with spray foam insulation, and you may have even used the foam that comes in pressured spray cans at home improvement retailers. This foam is know as one-part foam, meaning that it is one continuous mixture that is simply applied to the area in need. One-part foam is frequently used for sealing small gaps and cracks.

Today, each of the 50 states follows a different set of building codes making navigating these codes confusing, particularly for architects or builders that have projects in multiple states. In some cases, the building code changes significantly between the state and certain cities or counties within the state. For example, at the time of writing Arizona had adopted the 2015 IRC Building Code, however, Phoenix was on the 2012 IRC, IBC and IECC code. With the majority of states either on the 2009, 2012 or 2015 code, below are some high-level points to consider and about how spray foam insulation contributes.

Spray Foam Garage Door


Q. "I talked to a building product supplier for WALLTITE spray foam, he is suggesting to use 2" or 3" of closed cell-spray foam in the joists areas instead of the batts insulation. He says it will work with outboard rigid insulation. There is a location of a cantilevered floor area with steel beam so I may need to use spray foam to protect the steel beam. It would then be convenient continue to spray in the floor joist cavities and then apply 5" of polyiso outboard of the bottom cantilever floor sheathing."

Spray Foam Companies


The problem you saw with the closed cell foam pulling away like that is due to the heat of the foam was to hot. It was actually curing out and making foam before it could adhere to the wood. The installer wasn't reading his foam correctly. He should of stopped and turned down the heat on his hose temp. Also installers have to be aware that as the sun rises and the temp in attics rises the subtrates get hotter as well. This will cause the installer to adjust his heat when installing the foam as the temp changes thru out the day.   https://m.youtube.com/e/ggLAUsiuI_o
One of the high-tech insulation products being utilized these days is a foam-spray product called "Icynene," which is a foam that starts as two liquid components (a and b, if you will) that are heated up and sent through two hoses and meet at a tip of a gun where the magic begins. This is a thin film that expands to 100 times its volume in eight seconds, when it's permanently set up.

Before you decide on spray foam or another method of insulation, it's important to understand the superiority of spray foam compared to traditional materials. When compared to fiberglass batts, spray foam offers nearly double the R-value per inch, achieves air-sealing and insulation in one step, won't be damaged by mold or moisture, and won't settle, compress, or otherwise be damaged to the point it needs replacement.

Spray Foam On Roof Deck


United Coatings™ Roof Coat Elastomeric Coating is an effective coating for providing long-term reflectivity over a wide range of roofing substrates. The high reflectivity of Roof Coat Elastomeric Coating keeps the roof substrate cool, which not only helps prolong its longevity but also helps save on energy costs. Roof Coat Elastomeric Coating’s rich consistency uniformly covers the textured profile of various substrates, forming a flexible monolithic membrane that provides protection from normal weathering, aging, and ultraviolet exposure.

If your foam pulled away just a little bit, Jamie, and they were able to fix it with just a little bit of touching up, then it wasn't as bad as the house where I saw this problem. As the last photo above shows, it had pulled away significantly from the studs and rafters, and it was all over the house. This was closed cell foam, and interestingly, it didn't pull away from the horizontal framing members, just the vertical and sloped ones. They did some touch up, but that wasn't enough. I don't know how this one ended up getting resolved. I think maybe the contractor came back and sprayed cellulose on top of the foam.


Spray foam is available in two different types: open-cell spray foam which is usually $0.44 to $0.65 per board foot and closed-cell spray foam which is about $1 to $1.50 per board foot. The average cost to have spray foam professionally installed is about $2,316. This number can vary depending on whether the home being insulated is newly constructed. However, finished homes are not a good candidate for spray foam insulation but great for weatherization or an energy audit.   http://youtube.com/e/ggLAUsiuI_o?app=desktop

Wallis Spray Foam was started in 1997. We were one of the first Urethane spray foam providers in Parker and surrounding counties. Since 1997, Wallis Spray Foam has continued to provide Urethane services for residential and commercial markets in the North Central Texas area. Our company is based in Weatherford, Texas where we have a reputation of providing a professional, customer oriented service. Wallis will approach every job as its most important and complete the service in a timely manner. We only do the best quality service and no job is considered too small or too big.
Starting a new build (1 1/2 basement walkout), all 2x6 exterior walls w/ brick veneer in CZ3. Above grade, would like to do spray foam in 2x6 walls, 1/2" or 1" of rigid foam board on the exterior, and a 1" air gap. Will this require a house wrap or can I do w/o the rigid foam and go with a housewrap? Also, any recommendations about insulation strategies for the finished basement. Thanks!
The video below is from a house near Charleston, South Carolina that I visited recently, and you'll see that the homeowner in this case didn't get his money's worth. I knew immediately when I walked into the attic that something was wrong because it was hot up there. In a properly insulated spray foam attic, the temperature won't be much higher than the house temperature. 
Find spray foam contractors, suppliers, equipment, news, and technical information about spray foam insulation, foam roofing, and protective coatings. If you are a homeowner, builder/architect, or interested to get into the spray foam business, we have set-up special areas just for you. Check out our information packed Spray Foam Guides to learn more.
The video below is from a house near Charleston, South Carolina that I visited recently, and you'll see that the homeowner in this case didn't get his money's worth. I knew immediately when I walked into the attic that something was wrong because it was hot up there. In a properly insulated spray foam attic, the temperature won't be much higher than the house temperature. 
When it comes to weatherproofing your RV roof, the Flex Seal liquid roof is one of those we’re proud to recommend because it can be applied in all temperatures. It can also protect your camper roof from even the harshest weathers, including rain, snow and wind. With it, you can keep your roof protected from changing temperatures, eventually prolonging its lifespan. https://youtube.com/watch?feature=youtube_gdata&v=ggLAUsiuI_o
Spray polyurethane foam, or SPF, is the main type of 2-part, closed-cell spray foam used by insulation contractors. Large-scale insulation jobs require special equipment as well as safety gear to protect the installer from chemical fumes during installation. When the foam cures and hardens just several minutes after application, it's completely safe for as long as it stays in place. http://www.youtube.com/watch?v=ggLAUsiuI_o&feature=kp
The problem you saw with the closed cell foam pulling away like that is due to the heat of the foam was to hot. It was actually curing out and making foam before it could adhere to the wood. The installer wasn't reading his foam correctly. He should of stopped and turned down the heat on his hose temp. Also installers have to be aware that as the sun rises and the temp in attics rises the subtrates get hotter as well. This will cause the installer to adjust his heat when installing the foam as the temp changes thru out the day.   https://m.youtube.com/e/ggLAUsiuI_o
This stuff works GREAT ! I live in an older mobile home that had a lot of leaks when I moved-in. I worked for two years to locate and fix them all. Now I simply go over all of the repaired places once a year just to be sure everything is OK. NO LEAKS FOR 4 YEARS NOW!!  Others here use "sno proof" or something that does not stop leaks. When I tell them about my success, they don't seem to want to pay the$ for this superior product. Too bad!. I used the tape in  repairing the leaks.

My other question was gonna be this. We ripped all the drywall out after Hurricane Harvey and we found some latent termite damage from some time back. One of the common studs in one corner is pretty well eaten to shreds. I was gonna brace it but then I read about more modern framing practices and I read how each stud is a thermal bridge. So now I'm thinking that I won't bother with it because the house hasn't fallen down and the foam might help a little. Unless you say to brace the stud. Then I'll do it, Martin! :)

NOVA Spray foam did just as they promised and, more importantly, for the price they quoted. The two employees who ultimately installed the product were very nice, pleasant, and respectful. Bottom line: We are delighted with the install. Our house now holds a more stable temperature and no longer has hot spots. It used to be very difficult to cool our upstairs bedrooms; those days are gone! Pocketbook issues: For the last three billing cycles we have used approximately one third less electricity as the AC does not come on as often. Would we do this again? Yup! Do we recommend this installer? Yup! Do the neighbors think it’s cool? Yup!

How Much Does Spray Foam Insulation Cost

×